Topic · Fire alarm

Fire alarm systems

How fire detection and alarm systems are put together, what the panel is telling you, and what a facility team’s job is — and is not.

How it fits together

A fire alarm system detects fire (smoke, heat or flame detectors and manual call points), decides at the control panel, and warns people (sounders, beacons, voice alarm) while signalling other systems: releasing doors, stopping air handling units, recalling lifts and calling the fire brigade where connected.

Conventional systems wire devices in zones on radial circuits, so the panel knows the zone but not the device. Addressable systems wire devices on a loop, each with its own address, so the panel names the exact device. Loops are usually wired out and back to the panel, with isolators so a single short circuit takes out only a section.

Fire alarm systems are life-safety systems. Their design, installation, modification, servicing and certification must be done by qualified, authorised people following the National Building Code of India (Part 4), the standard the project was designed to (for example IS 2189) and the conditions of the fire NOC.

Life-safety system. This page explains how these systems work so you can understand, record and report. It is not a procedure for designing, modifying, isolating, testing or repairing them. That work must be done by qualified, authorised people following the National Building Code of India, the standard the system was designed to and the conditions of your fire NOC.

Conventional zone and addressable loopLeft: a conventional panel with one zone wired as a radial circuit through four detectors and ending in an end-of-line device; the panel knows only which zone is in alarm. Right: an addressable panel with a loop that leaves the panel, passes devices with individual addresses and returns to the panel, with isolators between sections so one short circuit affects only one section.Conventional: zone knownPanelzone 1SSHMEOLRadial circuit ends in an end-of-line device.Addressable: device knownPanelloop 1010203040506Loop out and back; isolators (◆) contain a short.S smoke · H heat · M manual call pointLife-safety system: changes only by qualified,authorised fire alarm engineers.
A conventional zone (radial circuit ending in an end-of-line device) beside an addressable loop that leaves and returns to the panel, with isolators between sections.

What a facility team should do

  • Treat every fault as urgent

    A fault or disablement means part of the building may not be protected. Record it in the log book, tell the responsible person and call the fire alarm maintainer.

  • Keep the log book

    Record alarms (real and false), faults, disablements, tests and service visits with date, time and who did what. Inspectors and maintainers rely on it.

  • Never leave zones disabled

    Disabling a zone for work must be planned, authorised, recorded and reversed as soon as the work ends, with extra fire watch if your procedure requires it.

  • Report false alarms

    Repeated false alarms from one device have a cause (dust, steam, cooking, wrong detector type). Report the device address and the conditions; do not cover or remove detectors.