Understanding PoE power budgets, with a worked example

PoE classes, why a switch can refuse power when the load fits, cable loss, and a worked example for a 16-port, 250 W switch with cameras, PTZs and an IP speaker — checked by class and by load.

A PoE switch has two limits: the number of PoE ports and a total power budget that all the ports share. Cameras that reboot at night when IR comes on, a PTZ that never powers up, or the last camera on a switch staying dark are usually budget problems. This guide explains PoE classes, where the “missing” watts go, and works through a full example checked two ways.

PSE, PD and classes

The switch (or injector) that supplies power is the PSE, power sourcing equipment. The camera, phone, access point or speaker that receives it is the PD, powered device. When a PD is connected, the PSE detects it and the PD announces a class, which tells the PSE how much power it may need. The IEEE 802.3 standards define the classes:

PoE classes: power at the switch port and guaranteed at the device
ClassStandardAt the switch (PSE)At the device (PD)
0802.3af (Type 1)15.4 W12.95 W
1802.3af (Type 1)4 W3.84 W
2802.3af (Type 1)7 W6.49 W
3802.3af (Type 1)15.4 W12.95 W
4802.3at (Type 2, PoE+)30 W25.5 W
5802.3bt (Type 3)45 W40 W
6802.3bt (Type 3)60 W51 W
7802.3bt (Type 4)75 W62 W
8802.3bt (Type 4)90 W71.3 W

Class 0 is “unclassified”: the device did not announce a class, so the switch must assume the full 802.3af figure. A camera’s datasheet gives its PoE class and its maximum power draw, often with and without IR, heater or wiper running. You need both numbers.

Where the missing watts go

The switch supplies more than the device is guaranteed because some power is lost as heat in the cable. The standards allow for a worst-case 100 m channel:

Cable loss allowed for in the standards
  1. 802.3af: up to 350 mA through a loop resistance of up to 20 Ω. Loss = I² × R = 0.35² × 20 = 2.45 W, so 15.4 W at the switch leaves 12.95 W at the device.
  2. 802.3at (PoE+): up to 600 mA through up to 12.5 Ω. Loss = 0.6² × 12.5 = 4.5 W, so 30 W at the switch leaves 25.5 W at the device.

These figures assume proper copper cable. Copper-clad aluminium (CCA) cable has much higher resistance, so more power is lost, the voltage at the camera sags, and devices brown out or reboot when their load rises. Use solid copper cable of the right category, and keep runs within 100 m.

Two ways a switch budgets power

  • By class (allocation): the switch reserves the full class figure for each port, whatever the device actually draws. A class 4 camera reserves 30 W even if it uses 12 W.
  • By actual consumption: the switch measures what each port draws (or negotiates a figure with the device over LLDP) and counts that against the budget.

Switches differ in which method they use, whether you can choose, and what they do when the budget runs out (usually they refuse power to the lowest-priority or highest-numbered ports). Because you rarely know how a replacement switch will behave years later, a good design passes both checks, or deliberately relies on consumption-based allocation that has been configured and documented.

Worked example: 16 ports, 250 W

A floor of a building is served by one 16-port PoE+ switch with a 250 W PoE budget (the figure in the switch datasheet for total PoE power, not the power supply rating). It feeds:

  • 12 dome cameras, class 3, datasheet maximum 6.5 W each with IR on;
  • 2 PTZ cameras, class 4, datasheet maximum 24 W each;
  • 1 IP horn speaker, class 3, maximum 10 W.
Check 1: ports
  1. 12 + 2 + 1 = 15 devices on 16 PoE ports. Passes, with one PoE port spare. Use a separate uplink port.
Check 2: budget by class
  1. Class 3 devices: 13 × 15.4 W = 200.2 W
  2. Class 4 devices: 2 × 30 W = 60 W
  3. Total reserved: 200.2 + 60 = 260.2 W against 250 W

Fails by 10.2 W. A switch that allocates by class will refuse power to at least one device.

Check 3: budget by actual load
  1. Domes: 12 × 6.5 W = 78 W
  2. PTZs: 2 × 24 W = 48 W
  3. Speaker: 10 W
  4. Total drawn: 78 + 48 + 10 = 136 W, which is 54 % of 250 W, leaving 114 W spare

Passes comfortably. Each device is also within its class: 6.5 W and 10 W are below 12.95 W, and 24 W is below 25.5 W.

This is the classic trap: the real load uses only about half the budget, yet the switch may still leave a camera dark. Nothing is faulty; the design simply did not check allocation.

Making the design pass

  1. Use consumption-based allocation if the switch supports it. Configure it, document it in the as-built, and keep the actual load well below the budget. Many designers keep actual load under about 80 % of the budget so that night-time IR, heaters and future additions fit.
  2. Set port priorities. Give critical cameras (entrances, cash areas) high priority so that if power ever runs short, the least important devices lose power first.
  3. Choose a larger budget. The same devices on a switch with a 370 W budget pass both checks: 260.2 W by class leaves 109.8 W spare, and 136 W by load leaves 234 W.
  4. Move high-power devices. Put the PTZs on another switch or on midspan injectors, so the class 3 devices fit within the original budget (13 × 15.4 W = 200.2 W).
  5. Check devices that exceed their class. A PTZ whose heater pushes it to 30 W cannot be run on class 4 (25.5 W at the device). It needs an 802.3bt class 5 or 6 port, a suitable injector, or local power as its datasheet allows.

The power budgeting lab runs these checks for your own devices, and the CCTV network builder lets you place cameras across several switches and see each budget.

Checklist

  • Take each device’s class and its maximum draw (with IR, heater and wipers) from the datasheet.
  • Check ports, budget by class, and budget by load; record all three in the design.
  • Check per-port limits: some switches offer PoE+ or 802.3bt on only some ports.
  • Use solid copper cable and keep runs within 100 m.
  • When sizing the UPS, add the switch’s own consumption to the PoE load, from its datasheet.
  • Label critical ports and set priorities before handover.

This guide is general technical information written for installers, engineers and facility teams. Check the manuals for your exact equipment and follow site safety rules. Brand names identify products only; Foxnet University is independent of the manufacturers mentioned.